Is Cat5E rated to be run in the walls of a commercial building without conduit?
laketime Senior Member May 31, 2010 #1 Is Cat5E rated to be run in the walls of a commercial building without conduit?
V Volta Senior Member Location Columbus, Ohio May 31, 2010 #2 As long as it is type CM, CMR, or CMP, and it complies with 300.4(D) and 300.11 per 800.24. Good design to comply with 300.4(B) too . . .
As long as it is type CM, CMR, or CMP, and it complies with 300.4(D) and 300.11 per 800.24. Good design to comply with 300.4(B) too . . .
C crazyboy Member Location NJ May 31, 2010 #3 It depends upon the type of insulation that is on the Cat 5. There is various different types with different ratings.
It depends upon the type of insulation that is on the Cat 5. There is various different types with different ratings.