in a warehouse from lets say from unistrut or a beam is it allowed to run sealtite down from that point and use clamp to secure to a machine 15 feet below. if not would a threaded rod down a few feet and sealtite strapped to it be ok? I read Article 350 covers sealtite. or does it have fmc or rigid only?

CAt 6 is what will be run to these machines, up to unistrut over to j-hooks into a tray and to an IDF.
 
Thanks but yes to 1st part on sealtite or 2nd aspect using threaded rod the. From it down with sealtite?
The threaded rod, I have used threaded rod, EMT and unistrut to make drops like that in the past. then minimal sealtight to the equipment 3-6 ft. See 350.30
 