in a warehouse from lets say from unistrut or a beam is it allowed to run sealtite down from that point and use clamp to secure to a machine 15 feet below. if not would a threaded rod down a few feet and sealtite strapped to it be ok? I read Article 350 covers sealtite. or does it have fmc or rigid only?

CAt 6 is what will be run to these machines, up to unistrut over to j-hooks into a tray and to an IDF.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Thanks but yes to 1st part on sealtite or 2nd aspect using threaded rod the. From it down with sealtite?
The threaded rod, I have used threaded rod, EMT and unistrut to make drops like that in the past. then minimal sealtight to the equipment 3-6 ft. See 350.30
 