solarken
NABCEP PVIP
- Location
- Hudson, OH, USA
- Occupation
- Solar Design and Installation Professional
I have seen a few references to this before but with conflicting info. I cannot find any clear information that suggests cat6 ethernet cabling carrying TCP/IP communications is considered class 1 or 2 or 3 circuits. THere is some verbiage that suggests that if Power over ethernet (POE) is enabled it may be considered class 2 or 3 power limited circuits. Without POE, it seems like it is just a communication circuit, which I believe is covered by article 800. I have a single 2-inch conduit that is buries to run a 10AWG 208V AC circuit in along with an ethernet cable and I am trying to figure out what is required as far as separation/protection within the conduit. For example, put the cat 6 in 1/2-inch ENT conduit and pull in with the THWN? Use MC cable for the power conductors and pull in ethernet with it? I don't want to damage the cat6, and it is probably at least a 50-foot run underground with a few 90's. Any code references would be helpful. 800.47(A) says Underground comm wires and cables, ...., in a raceway, handhole, ...., containing power conductors shall be in a section separated from such conductors by means of brick, concrete, or tile partitions, or by means of a suitable barrier.