Cathodic Protection 50Hz

Status
Not open for further replies.

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Question:
If you have a cathodic protection panel rated for 60 Hz will it work for 50 Hz?
Well, electrical cathodic protection systems are DC, so your unit is mainly a rectifier, which has nothing to do with frequency. So from that standpoint alone it shouldn't matter. The problem is, there are likely other components involved in the control and monitoring of it that might. We have no way of knowing, only the mfr will be able to answer that as mgookin said.
 

Besoeker

Senior Member
Location
UK
Photo attached.
I'm inclined to the view that it could work on 230V 50Hz but the manufacturers phone number is there. Why not give them a call?
Or post you question on their website:

http://www.matcor.com/productscategory/cathodic-protection-rectifiers/

MATCOR offers cathodic protection rectifiers in every standard configuration, including air-cooled, oil cooled and explosion proof. The rectifiers are available in almost any voltage and current output.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
In my opinion, a transformer rated 60 Hz at the same voltage at 50 Hz will be hotter since the magnetic flux increased -and even the resistance, due to reduced skin effect, will be less a bit. If the magnetic core-the laminates-is suitable designed it could be o.k. However the manufacturer has to be consulted.
 

topgone

Senior Member
In my opinion, a transformer rated 60 Hz at the same voltage at 50 Hz will be hotter since the magnetic flux increased -and even the resistance, due to reduced skin effect, will be less a bit. If the magnetic core-the laminates-is suitable designed it could be o.k. However the manufacturer has to be consulted.

Just reduce the supply voltage to 50/60 and you're good to go, IMO.
 