rbalex, I do not doubt your expertise in this area, so please do not be offended, I am just trying to understand. Article 501= Class I Locations, Article 500.5 Classification of locations, 500.5(B) Class I Locations, would that not require explosion proof equipment/material?
I overgeneralized the case a bit;
explosionproof equipment may be required in Division 2 if the equipment is arcing, sparking or high temperature(ASH) in normal operation like switches, luminaires or heaters. However,
explosionproof wiring methods are rarely required in Division 2. The limited cases are mentioned in Section 501.10(B)(4).
If Class I automatically required
explosionproof equipment, there is very little reason to even distinguish between Division 1 and 2.
Dealing with classified locations is typically a two-part process. First, the electrical area classification must be determined. Second, the proper equipment must be selected. Your installation is one of the few that classification can be directly determined from the NEC itself. [Art 515]