Astek
Member
- Location
- Mt Prospect, IL
I have a question regarding a video camera installation in a cattle barn that I am working on. What I am trying to figure out is if the installation is considered a Class II Division 2 installation.
Article 820 is a stand alone article, and 820.3 does not specifically reference article 500 or 547 (Agricultural Buildings). So, does this mean these sections do not apply and therefore the location is not subject to Chapter 5 rules?
On the other hand.. Article 547 would seem to classify the area as a Class II Division 2 hazardous location. (547.1(A) & 547.5(A))
So.... which one takes priority?
Article 820 is a stand alone article, and 820.3 does not specifically reference article 500 or 547 (Agricultural Buildings). So, does this mean these sections do not apply and therefore the location is not subject to Chapter 5 rules?
On the other hand.. Article 547 would seem to classify the area as a Class II Division 2 hazardous location. (547.1(A) & 547.5(A))
So.... which one takes priority?