Re: CAUGHT FLAT FOOTED
jb, I was hoping someone else would do it so I could pick on them, but I will do it, and let them pick on me.
Let's say the fundamental currents are:
Ia = Ip @ 0 deg.
Ib = Ip @ -120
Ic = Ip @ -240
That is, Ip is the RMS value of each phase current in the wye, and the separation is 120 degrees. This means the load is perfectly balanced. We don't know the PF and don't care.
Now sketch out the phasor diagram. It looks like the letter "Y" lying on its side--one leg pointing due east. Then using complex notation,
Ia = Ip + j0
Ib = Ip[-cos(60) -jsin(60)] = Ip[-0.5 -j0.866]
Ic = Ip{-cos(60) +jsin(60)] = Ip{-0.5 +j0.866}
Ia + Ib + Ic = 0
The operator "j" indicates the positive vertical component of a phasor, and "-j" indicates the negative vertical component of a phasor.
You can do this graphically and see for yourself. Just draw the phasor diagram as precisely as you can and break the 3 legs into horizontal and vertical components. You will see that the horizontal components cancel as do the vertical components.
Be aware that this exercise completely ignores any harmonic currents.