What would cause a GFCI trip on a floor heating thermostat when the cable tests fine? (resistance, continuity, and insulation test all pass)
What would cause a GFCI trip on a floor heating thermostat when the cable tests fine? (resistance, continuity, and insulation test all pass)
It seems to cause the nuisance trip when the heating cable warms up, system shuts off and starts back up again. This is typically when tripping occurs . . . I have tried swapping line voltage from one heated floor to another and the same one still trips . . . The GFCI is in the thermostat. Same manufacturing date on all 3 thermostats.
...The GFCI is in the thermostat...
The GFCI is in the thermostat. Same manufacturing date on all 3 thermostats.
Exchange the tripping thermostat with one of the others, and see if the trip behavior stays with the cable or moves with the thermostat.