tx2step
Senior Member
- Location
- North Texas, DFW area
I'm having to write a short requirement for adding a 200/3 and 400/3 CB into an existing 480/277V 1200A 3ph MLO panel (MDP). The service entrance from the padmount utility transformer to MDP is maybe 12' to 18' long, lug-to-lug. This will be CB's #4 and #5 in the panel, so it's still under the maximum # of 6. I want to make sure they select the correct AIC rating for the new CB's, without telling them what they should use (they're getting paid to do it). I'll be inspecting the installation, but they will be doing & are responsible for the design (not me). The installation will be done under the 2002 code. Is the following clear enough (or does it need refinement)?
"Provide documentation of the Available Short-Circuit Current at panel MDP, and the Interrupting Rating of each new circuit breaker to be added to panel MDP. Ensure circuit breaker short-circuit interrupting ratings exceed the available short-circuit current. Comply with 110.9 and 110.10."
"Provide documentation of the Available Short-Circuit Current at panel MDP, and the Interrupting Rating of each new circuit breaker to be added to panel MDP. Ensure circuit breaker short-circuit interrupting ratings exceed the available short-circuit current. Comply with 110.9 and 110.10."