In dwelling units NEC requires 3VA/sf for general lighting & receptacles. What is the minimum number of 15A breakers that are required to serve "general areas"? I was once told the rule of thumb was one 15A for every 500 sf. At the time I checked the math and it made sense to me. But now going through the math again...
15A breaker * 0.8 = 12A (derating for 15A circuit breaker)
12A * 120V = 1440VA (VA allowed to load on one 15A breaker)
1440VA / 3VA/sf = 480sf (sf allowed to be "loaded" onto one 15A breaker)
So it seems the rule of thumb should be one 15A circuit for every 480 sf - using 500sf is a hair too liberal a number. Am I correct?
Again I'm talking MINIMUMS here. Not "best practices". I wish that were not the case but gotta keep the clients happy.
Well, KIND OF wish it wasn't the case - staying tight to the code is a little exhilerating WHOOOO
15A breaker * 0.8 = 12A (derating for 15A circuit breaker)
12A * 120V = 1440VA (VA allowed to load on one 15A breaker)
1440VA / 3VA/sf = 480sf (sf allowed to be "loaded" onto one 15A breaker)
So it seems the rule of thumb should be one 15A circuit for every 480 sf - using 500sf is a hair too liberal a number. Am I correct?
Again I'm talking MINIMUMS here. Not "best practices". I wish that were not the case but gotta keep the clients happy.
Well, KIND OF wish it wasn't the case - staying tight to the code is a little exhilerating WHOOOO