oceanobob
- central coast California
- electrical and industrial contractor company owner
Time to run some electrical outlets at 120VAC: would like to run as a Multi Wire Branch Circuit (MWBC).
Having difficulty with the circuit breaker (CB) selection since the two pole breaker has the slash rating (120/240) but the three pole breaker does not. This has been confirmed by the salesrep at the supply house in contact w mfg and available literature.
Original idea was to have two sets of 'three hots and one neutral' for ea string w a #10 copper stranded conductor THHN in 3/4" EMT (thinwall) with one 20a CB Circuit Breaker with three poles for each set. Total thinking is/was six hots and two neutrals and two three pole circuit breakers.
But with the limitation of the 120/240 label for the CB looks like I need to go with 6 hots, three neutrals and three two pole circuit breakers. EMT limit getting close with 9 number #10s but OK.
Derating at 70% of the 90C 10's value is 28 amps (fyi number 12's at 21 amps but I'll prolly use the 10's) - this checks out.
Otherwise this plan now seems valid, yet am unable to understand why the three pole breaker is not available slash rated?