That is similar to the NEMA AB4 standard (See below, sorry about the format, tables never look good when you copy/paste them in here)
These times are "typical" for a 300% test for MCCB's, however the times may vary so it is better (And often required) to use the actual TCC for that specific breaker.
Range of Rated Continuous Current (Amperes) Maximum Trip Time in Seconds
For Each Maximum Frame Ratinga
< 250 V 251 ? 600V
0-30 50 70
31-50 80 100
51-100 140 160
101-150 200 250
151-225 230 275
226-400 300 350
401-600 - - - - - 450
601-800 - - - - - 500
801-1000 - - - - - 600
1001 ? 1200 - - - - - 700
1201-1600 - - - - - 775
1601-2000 - - - - - 800
2001-2500 - - - - - 850
2501-5000 - - - - - 900
6000 - - - - - 1000