CB sizing greater than 800A, 240.4(c)

Status
Not open for further replies.

plevymcs

Member
I have a Service Entrance with conductors sized for a 1500A. The load is multiple motors in a MCC. I want to use a PD frame size CB, thermal-magnetic breaker. Am I allowed to round up to 1600A for overcurrent protection, or do I use the next lower size available setting? The MCC bus is 1600A so the 1600CB size would not exceed the bus ampacity.

If I am allowed to round up, does the conductor ampacity need to be increased so it is greater than CB setting?

If I have a Thermal-Magnetic breaker, similar to Siemens SPD, and it is located in a manner that meets the requirements allowing an adjustable setting CB, do I set it for 1500A and call it a day?

Paul
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Since you're over the 800 amp threshold you can not round up. Sizing the OCPD to 1500 or less is required. This can be accomplished with a variable trip CB if all the conditions for its use are met.
 