The bottom line question: Do I need 10 or 8 THHN?

Situation:
RESIDENTIAL REMODEL.

SERVICE PANEL: Ambient temperature 105 to 113 degrees max (Albuquerque, NM) with 60 degree CB terminals.

BRANCH CIRCUITS: Three 20 amp circuits (bathroom and 2 small appliance circuits) run as follows:
Six 10 AWG THHN conductors run in 1 1/4? EMT from the service panel, up the side of the house, and bent 90 degrees into a 140 degree attic. The EMT continues 10 more feet and connects to a junction box (where there is finally a little headroom), from which the Bath and Kitchen are fed with three 12/2 NM cables.

Calculations:
FIRST TRY:
Table 310-16 says 10 AWG THHN has an ampacity of 40 amps.
Derate by .71 for 140 degree attic: 40 X .71 = 28.4 amps.
Derate by .80 for six parallel conductors in a conduit: 28.4 X .80 = 22.7 final ampacity.
Protect each circuit with 20 amp CB.

SECOND TRY:
BUT the CB terminals are only rated for 60 degrees, so I cannot use the 90 degree rating of the 10 AWG THHN and must use the 60 degree column. Luckily, a 8 AWG THHN has an ampacity of 40 amps at 60 degrees. So the calculation is the same as 10 AWG at 90 degrees: 22.7 amps final ampacity of 8 AWG at 60 degrees.

THIRD TRY:
BUT service panel (and the side ofthe house) is only 113 degrees not 140. Also the wires are no longer in a conduit.
So, can I use 10 AWG THHN at the 60 degree ampacity of 30 amps and derate the service panel portion of the wires at 105 degrees (with no parallel conductor derating): 30 * .71 = 21.3 final ampacity.


If the answer is not straightforward, maybe I should avoid inspector issues and just use 8 AWG.
 
I would comment on your thread but first must ask are you an electrician?
 
No, I am not. My municipality allows home owners to pull electrical permits.

I originally intended to simply move my Bath GFI receptacle. I got a permit. When I got into the wall, I saw that the house was originally built with a 14/2 NM cable and protected with a 20 amp GFI CB. Now I have to run a proper cable. Some previous owner has already added the Kitchen branch circuits with 1/2 inch EMT, but it was sloppily done and doesn't appear to have been inspected. I would like to clean up this mess.
 
I would like to answer your questions, but unfortunately this forum does not allow us to give advice to people who are doing their own electrical work.
 
Sorry, my mistake. So, that's why this forum seems so much better informed than the others - no dufusses like me!

Let me say, I have a lot of respect your profession (it's hard!), and I understand you limitting the forum to electricians.
 
hunanner said:
Sorry, my mistake. So, that's why this forum seems so much better informed than the others - no dufusses like me!

Let me say, I have a lot of respect your profession (it's hard!), and I understand you limitting the forum to electricians.
Dufuss or not, you have a better understanding of electrical work than most non-electrician homeowners I know :D
 
Please let me invite your attention to the following statement on the home page of this Forum:

This NEC? Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.

In accordance with that rule, I am closing this thread.
 