Since I work in a government facility, they decided that it would be best to have a contractor come in and remove some unused 120VAC circuits. He decided that he didn't need to check to see if the outlets were still live (they were a whole 6" away) and turned pliers into strippers. Minutes later, while pulling a "dead" cable (or so he thought) he cut another live cable. It didn't trip the 20A branch CB, or the 100A CB feeding that panel. Instead it tripped the 150A CB further up the food chain. It knocked out 19 radar displays and other equipment. This work was being done on midnights and nothing bad happened. If this happened during a period of high traffic, it could have been disasterous. The engineers explained that it was just the breaker with the fastest reaction time tripping first. Can someone point me in the right direction for having the smallest breaker tripping first? (faster reaction time, etc...) Regards, pete