Depends on what type system it's fed from. Omn a 240/120 single-phase, it is not a CCC. On a 3 phase system it would be.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Depends on what type system it's fed from. Omn a 240/120 single-phase, it is not a CCC. On a 3 phase system it would be.


I have to disagree. I would say no for both cases - 310.15(B)(4)(a) for single phase, and (b) for 3 phase.

Steve
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Steve, 310.15(B)(4)b says it must be counted as a current carrying conductor.

You are right, I didn't read that paragraph carefully enough. The neutral does count under 310.15(B)(4)b.

But if we go back to the original post, we had a "4 wire range". Doesn't that imply a 3 phase system? And if it is 3 phase, that means the neutral is not a CCC per 310.15(B)(4)a.

Steve
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
After a little more thought, maybe I didn't understand what was meant by "4 wire". Now I think I do.

4 wire means (2) hot wires, a neutral, and a ground. Is that right?? Now Augie and Raider's comments make sense.

I was thinking about 3 hot wires, and a neutral.

Steve
 

raider1

Senior Member
Staff member
Location
Logan, Utah
What is the intent? Is it due to the fact it is carrying unbalance from multiple phases?

If the neutral is only carrying the imbalance from 2 of the 3 phases of a 3 phase system, then the neutral will carry almost the same current as the ungrounded conductors, therefore you must count it as a current carrying conductor.

Chris
 

raider1

Senior Member
Staff member
Location
Logan, Utah
After a little more thought, maybe I didn't understand what was meant by "4 wire". Now I think I do.

4 wire means (2) hot wires, a neutral, and a ground. Is that right?? Now Augie and Raider's comments make sense.

I was thinking about 3 hot wires, and a neutral.

Steve

That is what I understood when the original poster said "4 wire range" 2 hots, 1 neutral and 1 EGC. I always think of a 3 wire range as a range that uses the neutral for bonding purposes.

Chris
 

A/A Fuel GTX

Senior Member
Location
WI & AZ
Occupation
Electrician
Yes, my intent was to reference a typical residential range circuit consisting of 2 phase conductors, 1 grounded conductor and 1 grounding conductor. I still have a hard time rationalizing the three phase scenario where the grounded conductor would be counted as a CCC. You still have a single phase load with 2 phase conductors and 1 grounded conductor.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
You still have a single phase load with 2 phase conductors and 1 grounded conductor.

But when you are dealing with a 3 phase system, the neutral conductor is connected to the common point of 3 ungrounded conductors. The only time the neutral will not count as a CCC on a 3 phase system is when it is carrying the unbalanced between all 3 phase conductors. If the neutral is carrying only the imbalanced current from 2 of the 3 phases the current on the neutral will be very close to that of the highest ungrounded conductor.

Here is the formula for finding neutral current for a 3 phase system.
ry400k.jpg


As you can see if Phase a was 10 amps and Phase b was 12 and Phase c 0 then the neutral would carry 11 amps.

Chris
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the neutral is only carrying the imbalance from 2 of the 3 phases of a 3 phase system, then the neutral will carry almost the same current as the ungrounded conductors, therefore you must count it as a current carrying conductor.

Chris

Yes, my intent was to reference a typical residential range circuit consisting of 2 phase conductors, 1 grounded conductor and 1 grounding conductor. I still have a hard time rationalizing the three phase scenario where the grounded conductor would be counted as a CCC. You still have a single phase load with 2 phase conductors and 1 grounded conductor.


You have to be careful when you use the term 3 phase system. The system that Chris is talking about is a 3 phase Wye system where the neutral would be a CCC. In a 3 phase, 4 wire Delta system the neutral would not be a CCC.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
You have to be careful when you use the term 3 phase system. The system that Chris is talking about is a 3 phase Wye system where the neutral would be a CCC. In a 3 phase, 4 wire Delta system the neutral would not be a CCC.

Good point, I am talking about a 3 phase Wye connected system. The answer I gave was in regards to 310.15(B)(4)(b) which is talking about a 4 wire, 3 phase Wye connected system.

Chris
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Good point, I am talking about a 3 phase Wye connected system. The answer I gave was in regards to 310.15(B)(4)(b) which is talking about a 4 wire, 3 phase Wye connected system.

Chris

I knew that's what you meant. :)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So to play it safe, when in doubt, count the neutral as a CCC.....

You could do that as long as it doesn't adversely impact your installation. The real concern is when using a single phase, 4 wire circuit from a WYE system. For everyday 120/240 volt systems you won't need to concern yourself about the neutral being a CCC.
 