Would the grounded conductor in a 4 wire range circuit be considered a CCC?
Depends on what type system it's fed from. Omn a 240/120 single-phase, it is not a CCC. On a 3 phase system it would be.
Steve, 310.15(B)(4)b says it must be counted as a current carrying conductor.
I agree, if this range circuit was on a 3 phase system you would need to count the neutral.
Chris
Steve, 310.15(B)(4)b says it must be counted as a current carrying conductor.
What is the intent? Is it due to the fact it is carrying unbalance from multiple phases?
After a little more thought, maybe I didn't understand what was meant by "4 wire". Now I think I do.
4 wire means (2) hot wires, a neutral, and a ground. Is that right?? Now Augie and Raider's comments make sense.
I was thinking about 3 hot wires, and a neutral.
Steve
You still have a single phase load with 2 phase conductors and 1 grounded conductor.
If the neutral is only carrying the imbalance from 2 of the 3 phases of a 3 phase system, then the neutral will carry almost the same current as the ungrounded conductors, therefore you must count it as a current carrying conductor.
Chris
Yes, my intent was to reference a typical residential range circuit consisting of 2 phase conductors, 1 grounded conductor and 1 grounding conductor. I still have a hard time rationalizing the three phase scenario where the grounded conductor would be counted as a CCC. You still have a single phase load with 2 phase conductors and 1 grounded conductor.
You have to be careful when you use the term 3 phase system. The system that Chris is talking about is a 3 phase Wye system where the neutral would be a CCC. In a 3 phase, 4 wire Delta system the neutral would not be a CCC.
Good point, I am talking about a 3 phase Wye connected system. The answer I gave was in regards to 310.15(B)(4)(b) which is talking about a 4 wire, 3 phase Wye connected system.
Chris
So to play it safe, when in doubt, count the neutral as a CCC.....