I recently was sent to a site with a problem with some CCTV suppression units on a camera system. A former security technician (holds a Journeymen's license) from my company had installed this lightning suppression setup. http://www.ditekcorp.com/product-details.asp?ProdKey=43
There is a DVR in the main building and two pan, tilt, zoom cameras on light poles in the parking lot. All the associated camera cabling runs in the same pvc conduit that also feeds the parking lot pole lights, the cables are not seperated from the lighting circuit in any manner. There is a suppression device out at each pole camera for protection of the camera and there is a suppression device for each camera in an electrical room where the CCTV cabling enters the building. At the poles the there is a ground rod in the ground with a bare copper #8 conductor running from the ground rod into the base of the pole up about 15" inside the pole and exiting out the side of the pole to a metal box mounted on the pole where the suppression device iis terminated.
On the building side in the electrical room there are the same suppression units and the power supplies for the cameras mounted inside a metal enclosure about 10" from cable entering the building. The power supplies are 24vac 50va open frame transformers fed with a line cord plug into a outlet (just hot and neutral) the ground is not bonded to the enclosure but instead connected to the lightning suppression ground terminals. This is the only "ground" for the lightning suppression that protects the DVR in the building.
With that said here is what happened.
On a sunny day there were some electricians working on the lighting circuit to the pole cameras trying to troubleshoot a problem with a couple of the lights. There were a two security technicians working on another camera on the opposite side of the building. The cameras were working in the morning and by the afternoon the all four lightning suppression devices were melted, and the two ports on the DVR that the pole cameras were connected to were dead. Of course nobody knows what happened. The DVR has been repaired, lightning suppression replaced, and the bare copper ground wire was replaced out at the poles with a jacketed Thhwn #6 by my company but I am concerned that this will happen again.
Is it plausible that a fault on the lighting circuit and what I have tried to describe regarding the CCTV suppression setup could cause damage to this DVR?
I am sure the current CCTV suppression configuration is not sufficient or code compliant.
Is article 820 the one that covers this type of system? I am trying track down what article and sections would cover this. I was pretty certain that a ground rod would be needed in the building and that it needs to be bonded to the buildings ground. I have to prove that this install is incorrect to my supperiors. Any help would be appreciated.
There is a DVR in the main building and two pan, tilt, zoom cameras on light poles in the parking lot. All the associated camera cabling runs in the same pvc conduit that also feeds the parking lot pole lights, the cables are not seperated from the lighting circuit in any manner. There is a suppression device out at each pole camera for protection of the camera and there is a suppression device for each camera in an electrical room where the CCTV cabling enters the building. At the poles the there is a ground rod in the ground with a bare copper #8 conductor running from the ground rod into the base of the pole up about 15" inside the pole and exiting out the side of the pole to a metal box mounted on the pole where the suppression device iis terminated.
On the building side in the electrical room there are the same suppression units and the power supplies for the cameras mounted inside a metal enclosure about 10" from cable entering the building. The power supplies are 24vac 50va open frame transformers fed with a line cord plug into a outlet (just hot and neutral) the ground is not bonded to the enclosure but instead connected to the lightning suppression ground terminals. This is the only "ground" for the lightning suppression that protects the DVR in the building.
With that said here is what happened.
On a sunny day there were some electricians working on the lighting circuit to the pole cameras trying to troubleshoot a problem with a couple of the lights. There were a two security technicians working on another camera on the opposite side of the building. The cameras were working in the morning and by the afternoon the all four lightning suppression devices were melted, and the two ports on the DVR that the pole cameras were connected to were dead. Of course nobody knows what happened. The DVR has been repaired, lightning suppression replaced, and the bare copper ground wire was replaced out at the poles with a jacketed Thhwn #6 by my company but I am concerned that this will happen again.
Is it plausible that a fault on the lighting circuit and what I have tried to describe regarding the CCTV suppression setup could cause damage to this DVR?
I am sure the current CCTV suppression configuration is not sufficient or code compliant.
Is article 820 the one that covers this type of system? I am trying track down what article and sections would cover this. I was pretty certain that a ground rod would be needed in the building and that it needs to be bonded to the buildings ground. I have to prove that this install is incorrect to my supperiors. Any help would be appreciated.