CCTV power and low voltage in same conduit

Status
Not open for further replies.

wirenut1980

Senior Member
Location
Plainfield, IN
Hello, Is it an NEC violation to have video cabling, and also the power wiring for the cameras only, in the same 2" PVC conduit? If a certain type of low voltage cable needs to be used, what kind does it need to be to be up to code? Is this in the NEC? Thanks. :)
 
Re: CCTV power and low voltage in same conduit

The signal feed cabling will be determined by the camera itself, most being coaxial with some newer market items utilizing Cat-5e.

In a perfect word, I would avoid having the power supplying line in the same conduit as the signal feeds as it will almost certainly bleed interference. Even 5-12v of current can cause interference when run parallel over 10+ feet next to the signal cable.

As for NEC articles, I don't have a reference handy to lookup any specifics.
 

bully

Member
Re: CCTV power and low voltage in same conduit

I have been using Simtra Cable which is a new cable UL listed and comply with the NEC code section 820.52(A)(1)exception No.1. I have been using this cable on several projects with excellence result. If you need info, let me know.
 