Cds air handler and elec heat

Status
Not open for further replies.

timmer

Member
Location
Phila PA
Occupation
engineer
Is there a low static pressure threshold where you would lockout elec heat because not enough air flow?with a VFD running on the air handler.
 

Eddie702

Licensed Electrician
Location
Western Massachusetts
Occupation
Electrician
If you buy a "packaged unit with the fan and heater built in they will sometimes have no protection against loss of air flow. I always thought this was foolish.

To my mind it should have a good differential air proving switch and /or a ct on the motor power to disable the heat when the motor shuts down.

Otherwise, plugged filters or a bad motor ,,,,,,,and then you buying new heater elements
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
If you buy a "packaged unit with the fan and heater built in they will sometimes have no protection against loss of air flow. I always thought this was foolish.

To my mind it should have a good differential air proving switch and /or a ct on the motor power to disable the heat when the motor shuts down.

Otherwise, plugged filters or a bad motor ,,,,,,,and then you buying new heater elements
I am surprised UL would list it that way.
 