question :1999 master electricians study guide.what is the demand load in va for a single range with a 18kw rating ,my answer was 18kw times 5% equals ???? the code states above 12kw must multiply 5% ,where did i go wrong ..........they have 4 answers (1)8,450,(2)9,560#(3)10,100(4)10,400 none of these come close to my answer...........
 

celtic

Senior Member
Location
NJ
It's not 18kw*5%...it's:
1999 NEC said:
T220.19
Notes: 1. Over 12 kW through 27 kW ranges all of same rating.
For ranges individually rated more than 12 kW but not more than 27 kW, the maximum demand in Column A shall be increased 5 percent for each additional kilowatt of rating or major fraction thereof by which the rating of individual ranges exceeds 12 kW.

Try that...see what you get...let us know :)
 

Mike Lang

Senior Member
Location
New Jersey
this might be confusing let me know if it helps

this might be confusing let me know if it helps

It says that over 12K you have to add 5% for each number over 12 . So if it is 18 Kw then the difference between 12 & 18 is 6 . Now multiply 6 x 5%= 30 %. Look in column C and the derating for 1 applicance over 12K is 8K. Now multiply 8Kw x .30= 2.4 Then the last step is to add the 2.4 to the 8Kw so the derated value is 10.4 Kw or 10400
 