I have read through a lot of posts after a search and only found one thread that specifically dealt with the question that I am about to ask; however, only a few weighed in with their interpretations. I hope that more will respond this time...lol.
In my area we have contractors using 4 AWG bare copper for concrete encased electrodes. The installation itself is fine; however, they generally leave only 12" or so out of the concrete. Then at the rough in stage they will splice another 4 AWG to this and continue to the panel.
Our current debate is: Should this splice be with an irreversible compression connector?
We have valid points on both sides of the argument, such as:
The CEE is no longer an electrode when it leaves the encasement. It then becomes a GEC and under code rule you have to splice a GEC with an irreversible or cadweld. (CEE denotes "encasement" and 20' at or near the bottom of the footing. The CEE is therefore the encased electrode. When it leaves the encasement it is no longer a concrete encased electrode).
Versus
The CEE is still an electrode when it leaves the encasement. Then the splice itself is a GEC to to grounding electrode splice and you can use the appropriate connector...i.e. it does not have to be irreversible. (We are generally seeing split bolt connectors used in this application).
_______________
I personally tend to side with the former. I believe that this connection should be irreversible. For example, if we have to splice 2 - 4 AWG conductors to run a ground to metallic cold water piping...the splice has to be irreversible. What is being done with the CEE is the identical connection: 2 - 4AWG conductors!
I haven't checked the actual listing requirements on split bolt connectors as the only time I ever used these when I used to be an electrician...lol...is to splice 2 ungrounded conductors together and the insulation around the split bolt had to match the insulation on the conductors. Perhaps split bolts are allowed to be used for 2 bare conductors. However, in the application listed at the beginning of this long post....can this be done?
Thanks to all who reply.
TXInspect
In my area we have contractors using 4 AWG bare copper for concrete encased electrodes. The installation itself is fine; however, they generally leave only 12" or so out of the concrete. Then at the rough in stage they will splice another 4 AWG to this and continue to the panel.
Our current debate is: Should this splice be with an irreversible compression connector?
We have valid points on both sides of the argument, such as:
The CEE is no longer an electrode when it leaves the encasement. It then becomes a GEC and under code rule you have to splice a GEC with an irreversible or cadweld. (CEE denotes "encasement" and 20' at or near the bottom of the footing. The CEE is therefore the encased electrode. When it leaves the encasement it is no longer a concrete encased electrode).
Versus
The CEE is still an electrode when it leaves the encasement. Then the splice itself is a GEC to to grounding electrode splice and you can use the appropriate connector...i.e. it does not have to be irreversible. (We are generally seeing split bolt connectors used in this application).
_______________
I personally tend to side with the former. I believe that this connection should be irreversible. For example, if we have to splice 2 - 4 AWG conductors to run a ground to metallic cold water piping...the splice has to be irreversible. What is being done with the CEE is the identical connection: 2 - 4AWG conductors!
I haven't checked the actual listing requirements on split bolt connectors as the only time I ever used these when I used to be an electrician...lol...is to splice 2 ungrounded conductors together and the insulation around the split bolt had to match the insulation on the conductors. Perhaps split bolts are allowed to be used for 2 bare conductors. However, in the application listed at the beginning of this long post....can this be done?
Thanks to all who reply.
TXInspect