I apologize in advance for the length, and if this question has been asked before. My repeated searches have yet to turn up anything.
_______________________________
Ok folks, now another question has arisen and we have the usual debate with people taking one side or the other...which will probably happen here as well...lol.
Anyway, I post this question for your thoughts and prehaps someone already knows where to find the correct information for what is listed as approved for a CEE. I haven't had time to check ASTM, UL, etc.
Here's the question:
Can tinned copper be used as a CEE?
As we all know the code says: Bare Copper
250.52 (A)(3) Concrete-Encased Electrode.
An electrode encased by at least 50 mm (2 in.) of concrete, located within and near the bottom of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (1⁄2 in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller
than 4 AWG. Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means.
However, it does not say bare tinned or untinned copper.
The reason this is coming up is....we see a lot of ground rings on radio towers where the engineer is spec'ing tinned copper because of its corrison resistance and ease of weld.
So let's post the code section for ground ring:
250.52 (A)(4) Ground Ring. A ground ring encircling the building or
structure, in direct contact with the earth, consisting of at
least 6.0 m (20 ft) of bare copper conductor not smaller
than 2 AWG.
Once again, I only see bare copper mentioned here. Bare tinned or untinned? The code is silent.
So, are we saying that because of the engineer's seal on the ground ring....tinned copper can be used in this application; however, tinned copper cannot be used for a CEE?
I've got a retired, well respected former Chief Elect Inspector of a large city saying that the tinned copper cannot be used as the CEE because it is not approved for this use.
So help me out folks.....Goggle searches have only turned up engineered ground rings thus far. Before I dig in a little deeper, does anyone already have this info?
For the record, I do know that bare tinned copper carries a little more resistance, so its not quite as good as untinned....but from what I have seen on the charts....the difference is minimal at best (0.02).
Thanks for reading!
TXInspect
_______________________________
Ok folks, now another question has arisen and we have the usual debate with people taking one side or the other...which will probably happen here as well...lol.
Anyway, I post this question for your thoughts and prehaps someone already knows where to find the correct information for what is listed as approved for a CEE. I haven't had time to check ASTM, UL, etc.
Here's the question:
Can tinned copper be used as a CEE?
As we all know the code says: Bare Copper
250.52 (A)(3) Concrete-Encased Electrode.
An electrode encased by at least 50 mm (2 in.) of concrete, located within and near the bottom of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (1⁄2 in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller
than 4 AWG. Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means.
However, it does not say bare tinned or untinned copper.
The reason this is coming up is....we see a lot of ground rings on radio towers where the engineer is spec'ing tinned copper because of its corrison resistance and ease of weld.
So let's post the code section for ground ring:
250.52 (A)(4) Ground Ring. A ground ring encircling the building or
structure, in direct contact with the earth, consisting of at
least 6.0 m (20 ft) of bare copper conductor not smaller
than 2 AWG.
Once again, I only see bare copper mentioned here. Bare tinned or untinned? The code is silent.
So, are we saying that because of the engineer's seal on the ground ring....tinned copper can be used in this application; however, tinned copper cannot be used for a CEE?
I've got a retired, well respected former Chief Elect Inspector of a large city saying that the tinned copper cannot be used as the CEE because it is not approved for this use.
So help me out folks.....Goggle searches have only turned up engineered ground rings thus far. Before I dig in a little deeper, does anyone already have this info?
For the record, I do know that bare tinned copper carries a little more resistance, so its not quite as good as untinned....but from what I have seen on the charts....the difference is minimal at best (0.02).
Thanks for reading!
TXInspect