No, concrete encased electrode can stand alone. Only the water pipe needs to be supplemented
Is that stated in 250.50?
Im trying to find the code verbage that tells me that.
And rod or pipe electrodes unless you can prove they are 25 ohms or less.No, concrete encased electrode can stand alone. Only the water pipe needs to be supplemented