I'm just wondering what your opinions are on this:

Do you think ceiling fan boxes should be required by Code to be wired with 3-wire cable, rather than 2-wire? I often find myself needing to replace the 2-wire cable feeding a ceiling box with 3-wire because the customers want to install a fan. 3-wire cable is required in order to be able to operate the light and the fan separately from the wall without using pull-chains on fans. If the builder doesn't want to install a fan right away, that's fine -- just cap off the red at the switch and ceiling boxes. This way, if someone else wants to install a fan in the future, they can do so without rewiring anything.

Whenever I wire a room that ceiling fans are commonly used in, I ALWAYS run 3-wire cable and a fan-rated box, whether the end customer intends to install a fan or not.
 

readydave8

re member
Location
Clarkesville, Georgia
Occupation
electrician
I'm just wondering what your opinions are on this:

Do you think ceiling fan boxes should be required by Code to be wired with 3-wire cable, rather than 2-wire? I often find myself needing to replace the 2-wire cable feeding a ceiling box with 3-wire because the customers want to install a fan. 3-wire cable is required in order to be able to operate the light and the fan separately from the wall without using pull-chains on fans. If the builder doesn't want to install a fan right away, that's fine -- just cap off the red at the switch and ceiling boxes. This way, if someone else wants to install a fan in the future, they can do so without rewiring anything.

Whenever I wire a room that ceiling fans are commonly used in, I ALWAYS run 3-wire cable and a fan-rated box, whether the end customer intends to install a fan or not.

We don't need for this to be required by code, no.

If I was looking for something to add to make service work more convenient (I'm not), I would require all panel boxes to be installed such that circuits could be added without disturbing or fishing behind finished walls.

But the NEC cannot consider every possible scenario. And I can charge more for fishing than I can for opening access panel.
 

JFletcher

Senior Member
Location
Williamsburg, VA
I'm just wondering what your opinions are on this:

Do you think ceiling fan boxes should be required by Code to be wired with 3-wire cable, rather than 2-wire? I often find myself needing to replace the 2-wire cable feeding a ceiling box with 3-wire because the customers want to install a fan. 3-wire cable is required in order to be able to operate the light and the fan separately from the wall without using pull-chains on fans. If the builder doesn't want to install a fan right away, that's fine -- just cap off the red at the switch and ceiling boxes. This way, if someone else wants to install a fan in the future, they can do so without rewiring anything.

Whenever I wire a room that ceiling fans are commonly used in, I ALWAYS run 3-wire cable and a fan-rated box, whether the end customer intends to install a fan or not.


This is above and beyond NEC minimums. If you can upsell it, by all means.
 

growler

Senior Member
Location
Atlanta,GA
I'm just wondering what your opinions are on this:

Do you think ceiling fan boxes should be required by Code to be wired with 3-wire cable, rather than 2-wire? I often find myself needing to replace the 2-wire cable feeding a ceiling box with 3-wire because the customers want to install a fan. 3-wire cable is required in order to be able to operate the light and the fan separately from the wall without using pull-chains on fans. If the builder doesn't want to install a fan right away, that's fine -- just cap off the red at the switch and ceiling boxes. This way, if someone else wants to install a fan in the future, they can do so without rewiring anything.

Whenever I wire a room that ceiling fans are commonly used in, I ALWAYS run 3-wire cable and a fan-rated box, whether the end customer intends to install a fan or not.

That is a design issue and not a safety issue.

There is nothing that is not safe about useing the pull chains or a remote, it's done all the time.

The code does not cover future expansion. You are required to meet code when you expand an electrical system but not before.
 

JDB3

Senior Member
I often use a fan rated box in areas where the owners may select a heavier than normal light fixture, especially in dinning or entry areas of some of the houses that I wire.
 

kwired

Electron manager
Location
NE Nebraska
I often use a fan rated box in areas where the owners may select a heavier than normal light fixture, especially in dinning or entry areas of some of the houses that I wire.
Nothing wrong with that. What was changed in 2011 was that if you run two separately switched ungrounded conductors to it you must use a fan rated box. That said I still believe this is design issues and shouldn't be a requirement. Might be wise to put fan rated box there, and many did just that before it was a requirement, but if there is not going to be a fan there NEC has no business requiring a fan box. Even if there is a fan there as long as it is independently supported from the box you still shouldn't need a fan rated box.
 