gary
Senior Member
- Location
- California
- Occupation
- Retired electrical contractor / general contractor
I have a client who wants me to install a "ceiling hugger" type fan in a small bathroom. I told him the NEC disallowed the installation of any part of a ceiling fan within 3' of a tub, but after re-reading the code I'm not so sure. Does the term "ceiling-suspended (paddle) fan" only apply to those types that hang from a down rod or does this article apply to all ceiling fans? I'm not sure I understand the rationale for the exclusion in either case.
410.10 (D) Bathtub and Shower Areas.
No parts of cord connected luminaires, chain-, cable-, or cord-suspended luminaires, lighting track, pendants, or ceiling-suspended (paddle) fans shall be located within a zone measured 900 mm (3 ft) horizontally and 2.5 m (8 ft) vertically from the top of the bathtub rim or shower stall threshold.