Cell Site Pole with Stadium Lighting

Status
Not open for further replies.

colosparker

Senior Member
Mixing power and light with wireless commmunications wiring in the same light pole. Do you use 830.133 A(1)(c) Exception 1, which allows separation by a permanent barrier or listed divider? Can you use MC for the lighting power and not violate NEC?
 
A lighting pole is considered a raceway per Article 410.
Separation is required.
For example, MC cable, or any chapter 3 wiring method can be used, Support is requiredm=, however, I would consider the wiring "fished"
 