Cement block wall with 7/8 metal furring straps secured to it

Merry Christmas

JJWalecka

Senior Member
Location
New England
I have to dress an MC cable down a block wall through a 7/8 furring strip and to an outlet. Will a nail plate at where the MC passes through the stud be adequate....or should the MC change to pipe coming down the block wall?

Thanks for your thoughts
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes a nail plate would work. If you keep the cable 1.25" away from the furring strip no protection required.
 