Can someone please the 5% limitation on the secondary of a 480-240/120V delta center-tapped transformer?
Is this 5% of rated kVA limitation in reference to the neural current on the center tap from unbalanced 120V L-N loads or is this in reference to the total connected kVA of 120V L-N loads connected between adjacent phases and centerpoint?
Transformer manufacturers seem to reference this in relation to total connected load but I’m wondering if this is a conservative rating that accounts for maximum unbalance current flowing on neutral?
Is this 5% of rated kVA limitation in reference to the neural current on the center tap from unbalanced 120V L-N loads or is this in reference to the total connected kVA of 120V L-N loads connected between adjacent phases and centerpoint?
Transformer manufacturers seem to reference this in relation to total connected load but I’m wondering if this is a conservative rating that accounts for maximum unbalance current flowing on neutral?