Im trying to figure out how to size wire to an air handler. The heat draws more of course, so i size it to the heat. In Table 210.2, it refers me to 422.12. Are there any other provisions to take into account, 125%of load for wire size, etc.? And am I in the right article?
Check out article 424
so the air handler is considered fixed space heating equip? whats the difference between central heating and fixed heating?
Most air handlers with electric heat are marked with MCA, minimum circuit ampacity, and MOCP, maximum overcurrent protection. The ratings will vary with what size heat strips, 5kw to 15kw for resi, you install and include the fan blower motor. 422.12 applies and yes it is a continuous load.
just out of curiosity, what if the unit didnt have mopd marked. what would i use 125%, 150%, 175%, 225% ?
I read what Dennis wrote and I think he is right. 424 is where to go. All units that I have seen are marked, see 424.28.
If you had a unit that was not marked, I guess you would size the motor using 430 and then figure out the amps for the heat, then size the total load as continuous and use 125%. I have never had to do this for an air handler, so I am not sure.