CFL lighting question....

Status
Not open for further replies.

Fulthrotl

~Autocorrect is My Worst Enema.~
i have a commercial account that i installed about 4 dozen Halo
remodel 6" can lights that take a CF18TE/835 4 pin lamp. i'm using
the lamps made by Ushio.

it's been 2 years since they were put in. i get a call today from
the customer, asking if i can check the installation 'cause the
lamps don't seem to last all that long... so i go take a peek, and
the lamp bases are somewhat discolored from heat... and those
4 dozen fixtures have gone thru about 18 lamps in 2 years....
but the package says these are supposed to last 7,000 hours.....
yea, right....:wink:

this halo fixture mounts the lamp base up. anyone else have problems
with this type of installation, with regards to service life?

thanks for any insight you may have.

randy
 

cadpoint

Senior Member
Location
Durham, NC
Sounds like a great reason to call the Rep. :roll:

There is 8760 hours in one year, 10 hours a day is 3650 hours.

Ha, great minds think alike.

You didn't say what was the enviroment ! ?

Instruct you clients to install lamps by the base...
 

ceb58

Senior Member
Location
Raeford, NC
Let me through in a crazy idea. The way I understand the OP the lamp is hanging down vertically. Correct? If this is the case could the lamps be vibrating loose causing the pins to lose some contact causing overheating and shortening the life of the lamp? But if you do the math 18 lamps out of 48 over two years is less than 2% per year.
 

ctmike

Senior Member
18 lamps out of 48 is 37.5 % but just remember stated hrs is an avg not a guarantee. complain to your dist. they will probley replace them
 

peter d

Senior Member
Location
New England
One thing I noticed about CFL's in remoted ballasted fixt.....errr..luminaires is that they get incredibly, ridiculously hot, particularly the 32 watt variety. I suspect heat may be a factor for premature lamp failure.
 

Fulthrotl

~Autocorrect is My Worst Enema.~
Sounds like a great reason to call the Rep. :roll:

There is 8760 hours in one year, 10 hours a day is 3650 hours.

Ha, great minds think alike.

You didn't say what was the enviroment ! ?

Instruct you clients to install lamps by the base...

what i'm gonna do is drop off a case of lamps, and a brand
new sharpie..... and mark the install dates on the bases...
and have him do the same... it'll keep him busy... and if
they start failing after six months burn time, the wholesale
house can start exchanging them. there's nothing else i
can really do at this point.... he's got 48 lights. they in
theory should last 2 years. that's 24 lamps a year.

if specific lamps are failing in a few months, that's another
thing, but without writing install dates on them, there's no
way i'm going to my wholesale house whining "dey burned out".

i have a brand new sharpie (green, no less) with his name on
it.... problem solved.

randy
 

barclayd

Senior Member
Location
Colorado
Please keep in mind that the Rated Life value means that, in this case, after 7000 hours of operation, HALF of the lamps will still be operational.
db
 

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
Dumb question to add - Do CFL's get a 3 hour hit, against each start, in regard to total lamp life (like a "normal" 4' flourescent tube)?
 

Besoeker

Senior Member
Location
UK
Sounds like a great reason to call the Rep. :roll:

There is 8760 hours in one year, 10 hours a day is 3650 hours.
[/COLOR]

Fulthrotl said eight hours a day, six days a week.
That would account for the disparity between your figure and his.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I have some mixed feelings on CFL lamps. Halo makes a can that is designed for the PLC type CFL lamps. They are expensive in comparison to the resi fixtures but you must realize that these latter fixtures have never been tested with CFL's and are approved as incandescent luminaires. I suspect the fixture manufacturer will give you no help on this. Good luck with the bulb manufacturer.
 

Fulthrotl

~Autocorrect is My Worst Enema.~
Dumb question to add - Do CFL's get a 3 hour hit, against each start, in regard to total lamp life (like a "normal" 4' flourescent tube)?

prolly. however, i've got two fixtures one on each side of my garage door,
and i put in 12 watt piggly wiggly CFL's into them, and did the math,
and it wasn't worth the $35 timer to turn them off... the timer would pay
for itself about 3 years after i die.

so i left them on.... the first one finally burnt out, after 3 years. 24/7.
 

cadpoint

Senior Member
Location
Durham, NC
Visitor, and that why your the engineer... :roll:

I was to excited that other's went on to show other some well rational numbers!

For some reason I went to 10 cause all I've known lately, I also thought and rationionalize (again) there would be some on that new vague flex time...
 

Besoeker

Senior Member
Location
UK
Visitor, and that why your the engineer...
And, despite my best endeavours, we still haven't (yet) got convergence on decimal, metric, SI, and the calendar.
Perhaps 10 hour days, 100 hour weeks, and 1000 day years are still some way off.
:D:D
 
And, despite my best endeavours, we still haven't (yet) got convergence on decimal, metric, SI, and the calendar.
Perhaps 10 hour days, 100 hour weeks, and 1000 day years are still some way off.
:D:D

The first 2 I have contemplated for some time... that means 100 second minutes, 100 minute hours, 10 hour days...

But the last one: 1000 day years... well either you got to re-define a year, or you got to talk to God about it... :roll:
 