CH Breakers HACR

Status
Not open for further replies.
HACR testing has been a standard part of UL489 for maybe the past 15 years or so.
Since this time, breakers are no longer required, by UL, to carry HACR labels.

Several manufacturers offer 'HACR' labeled breakers, at a price, for those few AHJ's that require one.
 
HACR testing has been a standard part of UL489 for maybe the past 15 years or so.
Since this time, breakers are no longer required, by UL, to carry HACR labels.

Several manufacturers offer 'HACR' labeled breakers, at a price, for those few AHJ's that require one.

Thus my question. I have an inspector that insists on seeing the HACR label. :roll:
 
Status
Not open for further replies.
Top