I was in a Cutler-Hammer Loadcenter yesterday. It was a 30-space / 30-circuit model of the CTL variety. In the panel were 4 CTL type tandems. It appears that the only difference between the CTL and non-CTL tandems in the CH line is the hook on the breaker. What this seems to mean is that it's physically possible to put a CTL tandem in a slot where it shouldn't be and the end result is just that the breaker doesn't hook on and is loose. In fact this is how I discovered this. I noticed that these breakers were wobbly as I was re-installing the cover.
I know Sq-D has the big metal hook with the slot for rejection and all the type BR, siemens, westinghouse, ... have the notch in the bus-stab and the deeper opening in the breaker.
The question - is the type CH not REALLY a rejection feature?
I'm confused.
As always, thanks,
Mark
I know Sq-D has the big metal hook with the slot for rejection and all the type BR, siemens, westinghouse, ... have the notch in the bus-stab and the deeper opening in the breaker.
The question - is the type CH not REALLY a rejection feature?
I'm confused.