D davelectric Member Feb 18, 2006 #1 Is it permissable to install a chandelier over a bath tub (no shower)? The fixture is to be relocated from an existing dining room and I don't know if its listed for a damp location.
Is it permissable to install a chandelier over a bath tub (no shower)? The fixture is to be relocated from an existing dining room and I don't know if its listed for a damp location.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Feb 18, 2006 #2 Re: Chandelier over Tub The answer is yes, but it would need to be at least 8' above the tub out of the tub zone.
Re: Chandelier over Tub The answer is yes, but it would need to be at least 8' above the tub out of the tub zone.
W wyatt Senior Member Feb 18, 2006 #3 Re: Chandelier over Tub to add that is the bottom of the chandelier 8' above top of tub
electrofelon Senior Member Location Cherry Valley NY, Seattle, WA Occupation Electrician Feb 18, 2006 #4 Re: Chandelier over Tub The 2002 handbook has a nice diagram of this, exhibit 410.1
T triphase Senior Member Feb 18, 2006 #5 Re: Chandelier over Tub 410.4(D) 05' NEC......8'up and 3'out