I have a circuit powered by a 250A, 480V CB. The circuit has a splice in it with 2x500KCMIL parallel cables being used be for approx. 1000ft and transitions to 2x4/0 AWG cables in parallel for another 1000ft. The voltage drop across each is acceptable but wondering if there is any issues or code restrictions in doing something like this. The conductors would meet the requirements of 310.10 - same length, material, cross sectional area and insulation. They will also use the same termination method and be located in the same raceway. The only thing I see is that the 4/0 AWG (230A @ 75 deg C) is lower than the Overcurrent Protection (250A). Not sure if that is a requirement for conductors >1/0 AWG.
Any advice you may have would be appreciated.