Hi All,
I have a client who needs to replace their overcurrent protection devices as they are obsolete.
The CTs are mounted externally of the transformer, so line currents are used.
The transformer is an arc furnace transformer, rated 3750 kVA, 13.8 kV primary.
The transformer primary can be reconfigured on the primary between delta (157 A) and wye (90 A). So winding current is rated for 90A.
The secondary is wye, with voltages varying between 400V to 87V through series and parallel bus connections. Let's say that the current rating is 12390 A for now.
The reason for the primary voltage changes is for varying the voltage on the secondary for the arc furnace application.
What I need to know is:
1) Do I need to provide two overcurrent settings for the transformer when the client needs to change the primary? Is this due to the line currents changing?
2) Does changing the primary configuration affect the kVA rating? i.e. for delta, my rating is 3750 kVA, and for wye, 3750/sqrt(3) kVA?
Thanks in advance.
I have a client who needs to replace their overcurrent protection devices as they are obsolete.
The CTs are mounted externally of the transformer, so line currents are used.
The transformer is an arc furnace transformer, rated 3750 kVA, 13.8 kV primary.
The transformer primary can be reconfigured on the primary between delta (157 A) and wye (90 A). So winding current is rated for 90A.
The secondary is wye, with voltages varying between 400V to 87V through series and parallel bus connections. Let's say that the current rating is 12390 A for now.
The reason for the primary voltage changes is for varying the voltage on the secondary for the arc furnace application.
What I need to know is:
1) Do I need to provide two overcurrent settings for the transformer when the client needs to change the primary? Is this due to the line currents changing?
2) Does changing the primary configuration affect the kVA rating? i.e. for delta, my rating is 3750 kVA, and for wye, 3750/sqrt(3) kVA?
Thanks in advance.