I know a number of people point to 690.13(C) to show that the NEC is implying that a PV supply side interconnection does not need to be treated as a service entrance. Section 690.13(C) in 2014 states:
(C) Suitable for Use. Each PV system disconnecting means shall not be required to be suitable as service equipment.
The new wording in 2017 is:
(C) Suitable for Use. If the PV system is connected to the supply side of the service disconnecting means as permitted in 230.82(6), the PV system disconnecting means shall be listed as suitable for use as service equipment.
While the NEC does not explicitly state if the supply side interconnection is a service entrance of a feeder tap this change would seem to indicate that they have changed the implied direction from feeder tap to service entrance. Why else have the disconnect rated for use as a service entrance if it's not also implied to install it as a service entrance? Why make the change?