Spent the last 2 days at our annual code convention in Raleigh. I really enjoy it and there are so many changes- some very costly in the 2017 NEC-- NC will probably amend many of them as I hear there are over 40 amendments at this point. Some of these changes we have talked about and some not.... NC probably won't adopt this code until at least 2018 late or more likely 2019.
We missed having Roger here this year but we had another forum guy show up--- I looked at him and said "You look like a guy who might own an electrical forum". He smiled and we shook hands--I said "I am Dennis Alwon" -- a smile and then I said laughing-"Mike, I am the chief moderator of your forum ".... I finally got a rise out of him. Obviously, I didn't expect him to know me but it was great that he was there with Bryan (sorry, forgot his last name), a new member of the mike holt team. Of course, Bryan Holland was up with the big cheeses answering all the questions... It was good seeing them all- Now if Roger and Mike Whitt were there we could have had a great reunion... LOL
The biggest in terms of cost is the gfci requirement in all non-dwelling kitchens for both 3 phase receptacles up to 100 amps and single phase receptacles up to 50 amps-- at 150v to ground or less...
They finally clarified how to measure the distances from sinks
They totally screwed up the peninsula countertop space. So instead of meaning to say that a receptacle at the wall can be used as the required receptacle for the peninsula they actually said that a receptacle must be installed along the long dimension of the countertop--- Isn't that where the doors and drawers are typically installed or the overhang for an eating area..... One at the end is technically not acceptable--- This is a big oops and I believe (Hope) most inspectors will not call this as written because it was not the intent.
There are tons of other changes which you can read here http://ecmweb.com/nec/2017-national-electrical-code-changes. You will need to sign up to the EC&M site which is free
We missed having Roger here this year but we had another forum guy show up--- I looked at him and said "You look like a guy who might own an electrical forum". He smiled and we shook hands--I said "I am Dennis Alwon" -- a smile and then I said laughing-"Mike, I am the chief moderator of your forum ".... I finally got a rise out of him. Obviously, I didn't expect him to know me but it was great that he was there with Bryan (sorry, forgot his last name), a new member of the mike holt team. Of course, Bryan Holland was up with the big cheeses answering all the questions... It was good seeing them all- Now if Roger and Mike Whitt were there we could have had a great reunion... LOL
The biggest in terms of cost is the gfci requirement in all non-dwelling kitchens for both 3 phase receptacles up to 100 amps and single phase receptacles up to 50 amps-- at 150v to ground or less...
2108(B) said:(B) Other Than Dwelling Units. All single-phase receptacles rated 150 volts to ground or less, 50 amperes or less and three phase receptacles rated 150 volts to ground or less, 100 amperes or less installed in the following locations shall have ground-fault circuit-interrupter protection for personnel.
(1) Bathrooms
(2) Kitchens
(3) Rooftops
Exception: Receptacles on rooftops shall not be required to be readily accessible other than from the rooftop.
They finally clarified how to measure the distances from sinks
210.8 said:For the purposes of this section, when determining distance
from receptacles the distance shall be measured as the shortest
path the cord of an appliance connected to the receptacle
would follow without piercing a floor, wall, ceiling, or fixed
barrier, or passing through a door, doorway, or window.
They totally screwed up the peninsula countertop space. So instead of meaning to say that a receptacle at the wall can be used as the required receptacle for the peninsula they actually said that a receptacle must be installed along the long dimension of the countertop--- Isn't that where the doors and drawers are typically installed or the overhang for an eating area..... One at the end is technically not acceptable--- This is a big oops and I believe (Hope) most inspectors will not call this as written because it was not the intent.
210.52(C)(3) Peninsular Countertop Spaces. At least one receptacle
outlet shall be installed at each peninsular countertop long
dimension space with a long dimension of 600 mm (24 in.) or
greater and a short dimension of 300 mm (12 in.) or greater. A
peninsular countertop is measured from the connected
perpendicular wall.
There are tons of other changes which you can read here http://ecmweb.com/nec/2017-national-electrical-code-changes. You will need to sign up to the EC&M site which is free