Changing color of wire with "phase" tape in a multiconductor cable

Status
Not open for further replies.

mooreaaryan

Member
Location
Bakersfield CA
Occupation
Electrician
Reading 200.6 it read to me that i can only change the color of the wire in a multiconductor if its the neutral. Is there a code that say i cannot change color or just a standard practice. i will have 4/c #14 3/c #12 all black with a bare ground or no ground.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
There are no restrictions on the re-identification of ungrounded conductors. Use of other than white and green as grounded and grounding conductors in a multi-conductor cable is permitted by the code rules. 200.6(E) Exception 1, and 250.119(B).
Since the grounded and grounding conductors are the only ones that require specific colors, there is no reason for there to be re-identification rules for ungrounded conductors.
 