C conmgt Senior Member Location 2 Phase Philly Jul 12, 2004 #1 Can I switch from Greenfield to Liquidtite in the middle of a run without using a box. If so, does the LFMC need to be metallic?
Can I switch from Greenfield to Liquidtite in the middle of a run without using a box. If so, does the LFMC need to be metallic?
ryan_618 Senior Member Location Salt Lake City, Utah Jul 12, 2004 #2 Re: changing conduit midrun Yes you may change types without a box. You would have to metal if the raceway is being used as an equipment grounding conductor.
Re: changing conduit midrun Yes you may change types without a box. You would have to metal if the raceway is being used as an equipment grounding conductor.