Have a existing 250 amp I-line breaker feed to air compressor .New air compressor only requires 200 amp circuit . If we add 200 amp fusible disc at new compressor fused at 200 amps would we have to change out 250 amp I-line breaker to a 200 amp????? Would this fall under a tap rule????????
 

ultramegabob

Senior Member
Location
Indiana
the breaker is protecting the feeders, the fuses are protecting the compressor where you reduced off of the feeders, I dont see anything wrong as long as you size your wire properly....
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Just for fun, let me play devil's advocate here.

Lets assume the original circuit was figured for a motor load.
For fun, a 75HP motor.. 480v 96 amps 120 amp branch circuit (#1) and the 250 amp breaker. (The breaker was the first overcurrent device so this is a branch circuit)

On the new compressor we add the fusible switch which becomes the branch circuit protective device. The original branch circuit is now a feeder. We have a #1 THHN feeder supplied by a 250 amp breaker.

Code Compliant ??

I've seen this approached more than 1 way in my life.
 