Changing old 120/120/208 Edison style breaker panel.

Status
Not open for further replies.

patricknola

Electrical contractor/Generac Dealer
Location
new orleans, La, United States
Occupation
Electrical contractor.
Hey guys, I just took a job to change out a very old 200 amp 120/120/208 volt panel. The old panel has (20) 20 amp single pole circuits, (3) 3 phase circuits, and (3) two pole circuits. Where do I land the high leg? Wouldn't every third breaker be 208 from hot to nuetral? TIA.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Sounds like you get it. Yes, an electrician must be aware of the high leg and terminate breakers accordingly.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Here's the relevant NEC code section.
408.3(E) Bus Arrangement.
(1) AC Phase Arrangement. Alternating-current phase arrangement on 3-phase buses shall be A, B, C from front to
back, top to bottom, or left to right, as viewed from the front of the switchboard, switchgear, or panelboard. The B phase shall
be that phase having the higher voltage to ground
on 3-phase, 4-wire, delta-connected systems. Other busbar arrangements
shall be permitted for additions to existing installations and shall be marked.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Wouldn't every third breaker be 208 from hot to nuetral? TIA.
In general, yes.


But it may depend on the panel.
40 years ago, panelboards, not loadcenters, often had breaker to bus connections (i,e, fingers) that were moveable. It was possible to build the panel with (6) 3-phase spaces and the rest of the 42 circuit panel all 1-phase.
 
Last edited:

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Hey guys, I just took a job to change out a very old 200 amp 120/120/208 volt panel. The old panel has (20) 20 amp single pole circuits, (3) 3 phase circuits, and (3) two pole circuits. Where do I land the high leg? Wouldn't every third breaker be 208 from hot to nuetral? TIA.
No one mentioned this but you won't have a high leg on a 208V service unless you meant 208V just on the high leg.
Be careful with "every 3rd breaker". You would need to start off with "B", which would be the 2nd breaker starting at the top. Then you can go every 3rd after that. It helps, if you have 120V loads on a high leg panel, to put tape on all the spots where B phase is. That way you can take a quick glance and see where the B phase is and avoid that for 120V circuits.
 

domnic

Senior Member
Occupation
Electrical Contractor
Number one rule identify what your working on or don't work on it !
 