I went to change out a GFCI receptacle today and had a strange experience. After putting in the new receptacle, it wouldn't set. I took care in making sure which conductors were line & load. I thought maybe the bare ground is touching the neutral so I checked that first. It was clear of the neutral so I thought maybe I got line & load reversed. To verify that I took the conductors off and turned the breaker back on. I was using a non-contact tester to find the hot. But I sounded off on both sets of conductors. So I got my meter and a test lamp to rule out a false reading. Turns out both sets of conductors were hot!
The receptacle had been double fed off the same circuit. The customer said he had noticed that part of the receptacle wasn't working and figured the GFCI was tripped. He said the reset button wouldn't work so he called me. I didn't check anything other than if the receptacle would reset, which it didn't. So knowing they fail, I just replaced it. He told me that part of it would work but the other part would not. It makes sense now that I know it was double fed. Apparently the side with the other feed was on the load side and it would work because it was live from the other feed.
This had to be an old GFCI because they used to fail closed. Meaning they would still work but the GFCI portion would not be protecting. New GFCIs have to fail open, which neither line or load will work.
I told the guy it was lucky the other feed was on the same circuit or he would have had 240V at the receptacle.
I just capped off the extra feed.
The receptacle had been double fed off the same circuit. The customer said he had noticed that part of the receptacle wasn't working and figured the GFCI was tripped. He said the reset button wouldn't work so he called me. I didn't check anything other than if the receptacle would reset, which it didn't. So knowing they fail, I just replaced it. He told me that part of it would work but the other part would not. It makes sense now that I know it was double fed. Apparently the side with the other feed was on the load side and it would work because it was live from the other feed.
This had to be an old GFCI because they used to fail closed. Meaning they would still work but the GFCI portion would not be protecting. New GFCIs have to fail open, which neither line or load will work.
I told the guy it was lucky the other feed was on the same circuit or he would have had 240V at the receptacle.
I just capped off the extra feed.