EC is changing out panels in an area full of townhouses. Does he have to use AFCI breakers, where it is now required, since he is going to a different type of panel :?
Barring any local amendments, using the 2014 NEC, IMO, no.EC is changing out panels in an area full of townhouses. Does he have to use AFCI breakers, where it is now required, since he is going to a different type of panel :?
That's what I was thinking.Barring any local amendments, using the 2014 NEC, IMO, no.
210.12(B) exception.
Barring any local amendments, using the 2014 NEC, IMO, no.
210.12(B) exception.
Apparently, he has found some CH "guts" that will fit in the FPE panels. He says that they are listed.
Any comments?
Apparently, he has found some CH "guts" that will fit in the FPE panels. He says that they are listed.
Any comments?