I have a bank customer that wants to change out an old Federal Pacific 208 3ph 4 wire breaker panel with no ground . rigid conduit to old service distribution panel .Some years ago a electrical contractor installed a new electrical service for the bank in another area of the basement about 40 feet away when the electrician did this you ran the distribution from the main new service in PVC conduit with no ground wire there's no possible way to to pull a new ground wire is it possible to run a separate conduit alongside for just the ground to the replacement panel . I was looking in the 2011 code book 250.134 exception no. 1 it says the equipment grounding conductor shall be permitted to be run separately from the circuit conductors is this been removed I misplaced my 14 code book don't have a new 17 and will this work for this situation