I want to re-purpose a #10 home run circuit. Can I put #10 onto a single pole 20amp breaker? The #10's run from the panel up to the attic about 20 feet total. Then I want to junction onto the #10 with #12 and run another 30 feet to a receptacle.Thanks
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
This is okay. It wouldn't hurt to find a way to tag the wire stating that there is #12 and to not use more than a 20a breaker.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Agree that you can do this. But you will need to make sure you have a #10 EGC, at least to the point where the 10 and 12 meet.
 

PhenixFord

Member
Location
Cabot, AR.
Occupation
Industrial Systems and Controls
I've "stepped" wire size due to voltage drop this way. I don't recall any rules about limiting the amperage?
 

wireday

Senior Member
Location
New England
Occupation
Master electrician
Thank you, Not sure why it was originally done this way,There are three circuits all together in the same EMT. They do share a #10 EGC. I know they always have been on the 20amp breakers.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Thank you, Not sure why it was originally done this way,There are three circuits all together in the same EMT. They do share a #10 EGC. I know they always have been on the 20amp breakers.
Could be for voltage drop. This is done all of the time.
 