I understand that Cuttler Hammer took over Challenger support. I have a situation where an electrician installed a 10KAIC rated Cuttler Hammer BR120 breaker in an old Challenger panel. After the City caught the owner for work without a permit, I'm called in to do the engineering. My fault calcs place the fault at the panel at just under 22KAIC. The Challenger panel lists several old Challenger breakers which would be series rated to 22KAIC, but of course they aren't available any more. Now I have found where the new BR120 breaker would be series rated with the upstream class T fuses in a Cutler Hammer load panel, but I can't find anything on Challenger. Now, CH does make a BRH120 that is fully rated 22KAIC. What would you do?