Chapter 9 Note 7

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Old age is messin' with me (again). I can't get my brain to comprehend Note (7) to Chapter 9 Tables.
Can someone translate this.
Specifically I was working on a teaching assignment where my conduit nipple fill allows 163.75 #12s (2.178 conduit area/0.0133 wire area).
In the real world this would make no difference but in the academic world with Note 7, would I be allowed 164 wires or 163 ?
 

Carultch

Senior Member
Location
Massachusetts
Old age is messin' with me (again). I can't get my brain to comprehend Note (7) to Chapter 9 Tables.
Can someone translate this.
Specifically I was working on a teaching assignment where my conduit nipple fill allows 163.75 #12s (2.178 conduit area/0.0133 wire area).
In the real world this would make no difference but in the academic world with Note 7, would I be allowed 164 wires or 163 ?

In the academic world, you have to round down on conduit fill calculations.

In the real world, you have to do so as well.

I'm guessing that this is 2" IMC, with wire type THWN-2? That is the closest my conduit sizer got, to the 60% fill limit for nipples. I also don't recommend depending on the 60% nipple fill limit, unless you really have to, because it takes skill to fit that wire through. In fact, with two wires it is impossible to fill higher than 50%, but two wires in a nipple is a blindspot of the code.

Another point: the diameters given for the common wire types are upper limits of what can be manufactured, and meet the industry standard for that kind of wire. If you have control over what manufacturer supplies the wire, you can use the nominal OD values from the datasheet, instead of the values in the chapter 9 tables. I don't recommend doing this, because it is rare that the person making the plan set has precise control of wire selection.

This can happen in my trade with PV wire, which doesn't have an NEC standard diameter table yet. I have to specify on the drawing set "PV Wire refers to Encore products. Cross check all conduit fill calculations, if a different manufacturer will be procured." And Encore PV wire is the most common in my area anyway, so it usually isn't a problem.
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
In the academic world, you have to round down on conduit fill calculations.

In the real world, you have to do so as well.

Thanks...
I assume from the "Note" that if my calculation allowed 163.81 I could go to 184.

(in my 'real' inspection world, ECs cram as many wires as physically possible in most nipples :))
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Thanks...
I assume from the "Note" that if my calculation allowed 163.81 I could go to 184.

(in my 'real' inspection world, ECs cram as many wires as physically possible in most nipples :))

My guess is that the number of wires they put in the nipple is less than what the table allows. It is really hard to get that many wires in there.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
(in my 'real' inspection world, ECs cram as many wires as physically possible in most nipples :))
Hi, Mr. Inspector. What do you want to see?.... What? Is that nipple overstuffed? I don't think so. Oh, look what's in front of it, a box of jelly doughnuts and some coffee. Why don't you sit a enjoy while I count the wires....Have one more I need to go get my calculator. Pretty sure it's not.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Hi, Mr. Inspector. What do you want to see?.... What? Is that nipple overstuffed? I don't think so. Oh, look what's in front of it, a box of jelly doughnuts and some coffee. Why don't you sit a enjoy while I count the wires....Have one more I need to go get my calculator. Pretty sure it's not.
TRUE! (Only I don't drink coffee).
Just stumpling thru teaching some classes and stumped myself on a self-made question :)

as if I didn't have enough troubles with Mike's Practice Exams
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Thanks...
I assume from the "Note" that if my calculation allowed 163.81 I could go to 184.

(in my 'real' inspection world, ECs cram as many wires as physically possible in most nipples :))


I agree and if it were 163.75 then you have to drop down to 163
 