Chapter 9 Table 1

Status
Not open for further replies.

wbalsam1

Senior Member
Location
Upper Jay, NY
  • A cable is treated as 1 conductor and can take up to as much as 53% of the raceway.
  • One conductor can also take up the same cross-sectional area of the raceway, namely 53%.
  • Two conductors can take up to 31%
  • Three or more can take up to 40%
  • In a nipple (less than 24" in length) one or more conductors can take up to 60%
Here's my question: Why 31% for 2 conductors which is less cross-sectional area than 40% for 3? In other words, it seems like for 2 conductors you must use less than for 3.
 
3 or more conductors tend to pull "flat" through a raceway. 2 conductors tend to twist and form a double-helix. Think "DNA". This double helix configuration adds tension to the pull thus requires more space than pulls of three coductors or more.
 
3 or more conductors tend to pull "flat" through a raceway. 2 conductors tend to twist and form a double-helix. Think "DNA". This double helix configuration adds tension to the pull thus requires more space than pulls of three coductors or more.

Thanks. I've wondered that for years...now I know. :smile:
 
Why 31% for 2 conductors which is less cross-sectional area than 40% for 3? In other words, it seems like for 2 conductors you must use less than for 3.

Looking at it from a geometrical standpoint helps to understand why...

csa2vs3.gif
 