Hi,
Wondering if someone can explain why we are allowed to use Table 8 for single phase AC circuits (small wire and unity PF) but not 3 phase circuits.
Thanks
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Table 8 addresses single conductors, not single phase circuits. It gives us the DC resistance of a single conductor. It does not address reactance, the other factor that combined with resistance gives us the total impedance. I am not sure why not.

Table 9 takes into account the impact of the conduit type, the resistance, the reactance, and the power factor, and gives us the net reactance ("Z").
 

shespuzzling

Member
Location
new york
Got it thanks. Related question re: Table 9. I understand how AC current in a conductor could induce eddy currents in steel conduit. How does this affect the reactance of the conductor as exhibited by the different reactance values for steel, PVC and aluminum conduit?
 