Residential customer purchased a Chargepoint EV charger for his garage and near future EV. He originally asked for 40AMP charging which would require #6 awg copper, a 40AMP breaker and a NEMA 14-50 receptacle to mate to the Chargepoint plug. He then changes his mind and wants it direct wired to get 50AMPS. So the wire size increases to #4 awg.
Upon checking the Chargepoint manual for direct wire, it shows that the field terminals for direct wire accept #6 awg. I emailed this to Chargepoint and they have yet to get back to me. Anyone run into this and if so what was your work around? Thanks in advance for any input.